Mr. Histor (Electrical)(OP)28 May 23 12:34
"....I have a 230V Power DB which is feeding the 230V control supply to PLC panel. The outgoing power circuits of this Power DB is equiped with MCB (6A) and RCCB (300mA). Today I noticed that the MCB tripped in the circuit which feeding to PLC control supply mentioned above. Please clarify why RCCB not done anything?"
I fully agreed with the advice by learned Mr.Pandit1.
I wish to add a little information for your consideration:
1. RCCB (300mA) may trips from >150mA on Earth fault only. It does NOT trip on over-current or short circuit current, up to any level.
2. A thermal magnetic MCB (6A) trips on thermal effect at any current > 6A with an inverse time delay, i.e. the higher the current, shorter the tripping time. The magnetic instantaneous trip depending on the tripping characteristics (i.e. B[3-5], C[5-10], D[10-20] times for the rated current) e.g. a 6A MCB with characteristic C would trip instantaneously between (5x6A) to (10x6A); otherwise characteristic D would be fine for most applications.
3. MCB is preferred instead of any type of fuses. In most cases, a 10kA MCB can switch back the supply immediately after the fault is rectified. In most cases, there is NO damage to the MCB.
Che Kuan Yau (Singapore)