Maximum Switching Surge Factor Calculation

Status
Not open for further replies.

Ballgame

Electrical
May 4, 2012
2
I'm trying to find the calculation for determining the Maximum Switching Surge Factor for a 230kV Transmission Line.

This term is defined in the National Electric Safety Code as a switching-surge level for circuit breakers corresponding to 98% probability that the maximum switching surge generated per breaker operation does not exceed this surge level, or the maximum anticipated switching-surge level generated by other means, whichever is greater.

Anyone familiar with a methodology or calculation for coming up with this value??

Thanks
 
Replies continue below

Recommended for you

Sorry,I cannot find anywhere in NESC where "Maximum Switching Surge Factor" is defined. Could you pls. indicate the chapter no.?
 
Section 232D3a

(In the 2011 edition of NESC it is on page 93 about 2/3 of the way down the page.)
 
Yes I found it, thanks.But I think you have to see:
thread238-297714
and here the cuky2000 answer.
 