3-7.5.3 Test Connection.
When backflow preventers are installed in fixed fire protection systems, test connection must be provided downstream of all backflow prevention valves for flow tests at system demand."
NFPA 13-2007, 8.17.4.6.1 "means shall be provided downstream of all backflow prevention valves for flow tests at system demand"
The appendix A.8.17.4.6.1 states "can be performed with a test header or other connection downstream of the valve." The appendix also suggests that a supervised bypass valve around the FDC check is acceptable. It doesn't say anything about using a flange or removing the clapper.
I personally think a tee with a supervised valve and a cap, a supervised bypass around the FDC check valve, a supervised valve with a simple test connection, or a test header with individual hose valves is good enough.
I understand most people interpret the above NFPA 13 passage to allow use of the FDC with clapper removed or a grooved flange for doing forward flow tests, since that is what is done for the NFPA 25 flushing of the lead in, but I don't consider that to be an NFPA 13 required "means provided" since you have to take the entire system out of service rather than just hooking up valves and hoses and then quickly opening a valve.. On a single riser setup you'd have to drain the whole system if the BFP is used as the system control valve.
The good thing is the UFC has that covered in greater more prescriptive detail (rather than a shady wording 'means provided'), and this helps increase the chances this will actually be tested per NFPA 24..