Maximum No. Of Systems from Ring Main Spur

Status
Not open for further replies.

DTR

Mechanical
Joined
Oct 30, 2002
Messages
21
Location
GB
Can anyone please advise me if there is a restriction on the number of Fixed Fire Protection Systems (Deluge Waterspray)that can be supplied from a spur off a Yard Ring Main.

I thought there was something in NFPA 850 but I can't find it, my concern is the number of systems that may be isolated simultaneously.
 
There is nothing that I am aware of that limits the number of systems being supplied by a single lead in. If I recall correctly, I believe that Factory Mutual recommends no more than 4 risers...but that could be old information.

We typically try to limit to 4 or 6 risers. Simply because the cost to run overhead bulk piping for any more systems will exceed the cost for an additional lead-in to the building from the underground loop.
 