sparkie93
Mechanical
- Sep 1, 2009
- 2
Help! I haven't touched my heat transfer book since 1985!
I'd like to know if I'm approaching this correctly. We have a 15" panel mount PC to be mounted to the lid of a polycarbonate enclosure (Hoffman type enclosure) and want to be sure it doesn't get too hot.
Dimensions: 22" x 15" x 7" (1178 in3 surface area) enclosure 3/16" thick. Heat transfer rate is 30 watts. Maximum internal temp allowed is 60deg C. Ambient temp (meat processing plant) could range from 0 - 30 degC.
Working backwards through the formula q = k*A*(T1-T2)/L and assuming 60degC for a worse case internal temp gives me 59.87degC. So as long as ambient is under this temp I'm fine.
Is this the correct approach? Does the formula really apply to a volume rather than just a basic area (I used the external area of the enclosure and ignored the fact that the face of the PC will be exposed to the ambient environment), or is there a more correct formula(s) to being using?
Thanks,
Robert
I'd like to know if I'm approaching this correctly. We have a 15" panel mount PC to be mounted to the lid of a polycarbonate enclosure (Hoffman type enclosure) and want to be sure it doesn't get too hot.
Dimensions: 22" x 15" x 7" (1178 in3 surface area) enclosure 3/16" thick. Heat transfer rate is 30 watts. Maximum internal temp allowed is 60deg C. Ambient temp (meat processing plant) could range from 0 - 30 degC.
Working backwards through the formula q = k*A*(T1-T2)/L and assuming 60degC for a worse case internal temp gives me 59.87degC. So as long as ambient is under this temp I'm fine.
Is this the correct approach? Does the formula really apply to a volume rather than just a basic area (I used the external area of the enclosure and ignored the fact that the face of the PC will be exposed to the ambient environment), or is there a more correct formula(s) to being using?
Thanks,
Robert