It's interesting how the scope of these rules is lacking
If you have two janitor closets 210 sq. ft. each, in an otherwise light hazard area, adjacent to each other, with a wall between them that does NOT go all the up
If you have two janitor closets 210 sq. ft. each, in an otherwise light hazard area, adjacent to each other, with a wall between them that DOES go all the up
If you have two janitor closets 210 sq. ft. each, in an otherwise light hazard area, 10 ft. from each other separated by a light hazard room
3 scenarios. The standard (13-2013) literally says:
6.3.7.6 Nonmetallic pipe listed for light hazard occupancies shall be permitted to be installed in ordinary hazard rooms of otherwise light hazard occupancies where the room does not exceed 400 sq. ft.
Since each janitor closet is a room, one would assume not to calculate the areas together. Using common sense, one might calculate the areas together based on if there is no light-hazard area separating them. It might also change depending on if walls go all the way up or not.
What happens if you have a 2 ft. light hazard separation instead of 10 ft. separation? What happens if it's 1 inch? What happens if you have 20 janitor closets all separated by 400' of light hazard areas, or 20 janitor closets adjacent to each other, or 20 janitor closets separated by 1 ft. of light hazard areas.
I understand that given experience and common sense, one can usually arrive at an answer most AHJ's would agree with, but it just seems impossible to get an accurate interpretation when the intent/background info of each rule is missing.