356.12 Uses Not Permitted. LFNC shall not be used as
follows:
...
(3) In lengths longer than 1.8 m (6 ft), except as permitted
by 356.10(5) or where a longer length is approved as
essential for a required degree of flexibility
So because a lot of people connect motors this way in order to facilitate the vibration, confined spaces etc., some people think it is a "rule" that the disconnect (or controller) must be within 6 ft.
dpc,
I have to admit that in all these years, I never noticed that! Of course, I have never needed to address it because I cannot think of a project where the issue came up. I have always either built the disconnect into the controller, or mounted one right next to it.
Whew... good to know I was following the rules...
"Will work for (the memory of) salami"