Nov 16, 2011 #1 hello12345hello Structural Joined Apr 25, 2011 Messages 50 Location US I have new W-beam lintel sits on existing unreinforced masonry wall. reaction is 10 kip. What is allowable bearing stress for URM. Wall is 6in thick. Do i have to use same 0.25f'm.
I have new W-beam lintel sits on existing unreinforced masonry wall. reaction is 10 kip. What is allowable bearing stress for URM. Wall is 6in thick. Do i have to use same 0.25f'm.
Nov 16, 2011 #2 msquared48 Structural Joined Aug 7, 2007 Messages 14,745 Location US Bearing on the full area of the wall, if it is special inspected, then the answer is yes. If it is not specially inspected, then you are only allowed half that value. Sounds like you're in this range to me. Mike McCann MMC Engineering Upvote 0 Downvote
Bearing on the full area of the wall, if it is special inspected, then the answer is yes. If it is not specially inspected, then you are only allowed half that value. Sounds like you're in this range to me. Mike McCann MMC Engineering