Masonry Shear Wall Horizontal Reinforcements 1

Status
Not open for further replies.

HofOblivion

Structural
Joined
Dec 15, 2014
Messages
13
Location
US
Hello everyone,

The section 21.9.2.2 of ACI 318 dictates "At least two curtains of reinforcement shall be used in a wall if a [factored shear demand] exceeds 2Acv(lamda)sqrt(f'c)." This obviously applies to concrete shear wall designs.

Is there a similar limitation to masonry shear wall designs?

Thank you in advance.
 
There sure is. Check out ACI 530/TMS 402 for the requirements.
 
@mike20793, I read through the MSJC-2011 chapter 3, but I couldn't find the section. Am I looking at the wrong area?
 
In the 2011 version, the seismic requirements are outlined in Section 1.18.
 