I am checking a masonry block supporting soil and lateral load the wall is 2.8-meter-high and span around 4 meter length, it is reinforced by 2HD16@400 centres.
That ratio is exceeding the balanced as I find a =44.7mm while a balanced =41.6 and according to the NZ standards which should be much same as other it is only allowed to be 0.75of the balanced section.
Is any max ratio for steel in walls or the ductile failure is not governing?
That ratio is exceeding the balanced as I find a =44.7mm while a balanced =41.6 and according to the NZ standards which should be much same as other it is only allowed to be 0.75of the balanced section.
Is any max ratio for steel in walls or the ductile failure is not governing?