I have never been fully confident that I am using the shear capacity equation of a CMU wall correctly-
ACI 530 3-18
Vn= Vm+Vs where
Vm = [4 - 1.75(Mu/Vudv)]An SQRT(fm')+.25Pu. I dont count the face shells of blocks towards An, but have seen this done in sample calcs - am I being too conservative?
and
Vs= .5*(Av/s)fvdv
Do we count reinforcing boardering openings (windows and doors) towards Av or just consider our nominal bar (say #5s at 48" oc)?? For dv, again, do we consider face shells as contributing?
On another note, I am unable to find a code minimum for beam bearing on CMU walls, although I'm sure it is referenced somewhere. I am responsible for designing a retrofitted hoist beam embedded in 4" CMU walls at each end but cannot penetrate exterior face shells so I need to determine how rugged of a steel support I will anchor to these walls to accomodate the beam.
Thanks,
VTEIT
ACI 530 3-18
Vn= Vm+Vs where
Vm = [4 - 1.75(Mu/Vudv)]An SQRT(fm')+.25Pu. I dont count the face shells of blocks towards An, but have seen this done in sample calcs - am I being too conservative?
and
Vs= .5*(Av/s)fvdv
Do we count reinforcing boardering openings (windows and doors) towards Av or just consider our nominal bar (say #5s at 48" oc)?? For dv, again, do we consider face shells as contributing?
On another note, I am unable to find a code minimum for beam bearing on CMU walls, although I'm sure it is referenced somewhere. I am responsible for designing a retrofitted hoist beam embedded in 4" CMU walls at each end but cannot penetrate exterior face shells so I need to determine how rugged of a steel support I will anchor to these walls to accomodate the beam.
Thanks,
VTEIT