I have never been fully confident that I am using the shear capacity equation of a CMU wall correctly-
ACI 530 3-18

Vn= Vm+Vs where

Vm = [4 - 1.75(Mu/Vudv)]An SQRT(fm')+.25Pu. I dont count the face shells of blocks towards An, but have seen this done in sample calcs - am I being too conservative?

and

Vs= .5*(Av/s)fvdv

Do we count reinforcing boardering openings (windows and doors) towards Av or just consider our nominal bar (say #5s at 48" oc)?? For dv, again, do we consider face shells as contributing?


On another note, I am unable to find a code minimum for beam bearing on CMU walls, although I'm sure it is referenced somewhere. I am responsible for designing a retrofitted hoist beam embedded in 4" CMU walls at each end but cannot penetrate exterior face shells so I need to determine how rugged of a steel support I will anchor to these walls to accomodate the beam.

Thanks,
VTEIT
 
Replies continue below

Recommended for you

If the face shells are mortared, then yes, count on them.

I'm home again today, so I don't have any references in front of me, but masonry bearing is typically limited to 0.25f'm.

As for bars around openings, I'm assuming you mean the horizontal bars above/below openings. I wouldn't count on them as part of your Vs.
 