Still unclear about what your asking.....
However, if your speaking about pipe inverts.....general rule of thumb is 1m max between inverts. If invert separation needs to be greater than 1m, use a drop structure. Also contact your local governing agency, they might have specific requirements.
If your speaking specifically to the installation during construction, typically the pipe opening's in manhole are quite larger than required, contact your manhole manufacturer for specific details. A permanent seal is then formed between the manhole and pipe by either a gasket or concrete parging.
Hope this helps.
Ryb01