Refer to the Ontario Provincual Building Code - the first step is to determine the vintage of the Apartment building - what year it was built - then you need to go to the Library and get a copy of the Ontario Building Code that applied at the time the building was constructed. I'll say this "generally" - since the late 1980's there has been a Building Code requirement to provide a minimum of 0.35 air changes per hour (ACH) for each suite. "Generally" the acceptable industry practice is to provide that amount of air via the corridor ventilation supply, hoping that the air enters the suites via the doors as each suite uses it's range hoods or bathroom exhaust fans. Typically I've seen the rule of thumb to be anywhere between 60 to 80 CFM (cubic feet per minute) of supply air per suite on each floor as the design airflow for the corridor ventilation supply sizing.
Recent studies have shown that, in fact, 60% or more of the corridor ventilation air is leaking up stair and elevator shafts and not even getting to the suites (by the way - in the last 20+ years of this practice, no one has yet to answer my question - how does the corridor air "leak" through the Code required fire and smoke-proof Suite Door....?). Current trends are heading towards new buildings using in-suite heat recovery ventilators, or in the case of suites with fan-coils or heat pump air conditioners, they will have a balanced fresh air supply ducted to the in-suite air conditioner. Then the corridor ventilation air supply can be reduced to a small amount to just pressurize the corridor for cooking odour control between suites.