Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

major error fault for slc-500

Status
Not open for further replies.

cvargas345

Electrical
Oct 25, 2007
7
Can someone explain to me what the major error S:6 155h means for a AB SLC-500. The error description box states that the discrete I/O module that is required for the user program has the wrong I/O count. This could mean a specialty card driver is incorrect. I am kind of new to plcs so I would appreciate it if someone could perhaps explain this to me. I having trouble understanding the terminology. Thanks in advance
 
Replies continue below

Recommended for you

Product(s):
1747-L5xx SLC Modular Hardware Style Controllers (SLC 5/01, 5/02, 5/03, 5/04 and 5/05)
RSLogix 500 Programming Software


Problem/Symptom(s):
- Error
"Discrete I/O module in slot XX which is required for the user program is detected as having the wrong I/O count.
This could also mean that a specialty card driver is incorrect."
- Error Code S:6=xx55h
- where xx (hex) is the Slot Number of the card/module in question
(Hex=Decimal; 0A=10, 0B=11, 0C=12, ...etc)


Advice; Reference Manual (1747-rm001):

Error Code (Hex)
xx55

Description
A discrete I/O module required for the user program is detected as having the wrong I/O count.
This code can also mean that a specialty card driver is incorrect.

Probable Cause
- If this is a discrete I/O module, the I/O count is different from that selected in the I/O configuration.
- If this is a specialty I/O module, the card driver is incorrect.

Recommended Action
- If this is a discrete I/O module, replace it with a module having the I/O count selected in the I/O configuration.
Then, clear the fault and run, or
- change the I/O configuration to match the existing module, then reload the program and run.
- If this is a specialty I/O module, refer to the user manual for that module.


Additional Advice:

A)
- make sure the Module is placed/seated correctly
- turn OFF the power to the Chassis, then push the module all the way in
- restore power to the Chassis

B)
- there may be a defective Slot on the Chassis Backplane
- as a test, try using the module in another Slot on the Chassis Backplane
- use the RSLogix 500 >> I/O Configuration to drag the module from its Slot to another spare Slot
- if you drag the module, then RSLogix500 should offer to change all the addressing automatically
- turn OFF the power to the Chassis, then swap the Module to its new configured Slot
- restore power to the Chassis

C)
- if using an Extended Local Chassis
- make sure the Interconnect Cable (1746-Cxx) is connected correctly between the two Chassis
- make sure the Extended Chassis is powered by its own Power Supply (1746-Px)

D)
- check the Ladder Project (.ACH .RSS) file
- go to RSLogix 500 >> I/O Configuration
- select the module in the Slot that has the problem
- press [Adv Config] button
- check to make sure it has the correct settings for Input (xx) and Output (yy)
Scanned Input Words : xx
Scanned Output Words : yy

E)
- there could be a problem with the Chassis Backplane
- replace the Chassis


 
Rockwell has a decent website to find some of this information as well. Go to and click on knowledgebase. You will have to register. Also, you can click on the 'Literature' hyperlink and do a search on SLC User Manual. You will eventually be able to find a manual that will explain to you what that code means.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor