BronYrAur
Mechanical
- Nov 2, 2005
- 799
I'm asked to resolve a problem where a chiller isn't receiving it's minimum flow at all times which is causing problems. The system serves several unit ventilators each with 2-way on/off valves. When the units aren't calling for cooling, the valves are closed.
The chiller has a minimum flow requirement of 119 GPM, and they want the chiller to operate even if only 1 unit ventilator is calling, which would be only about 6 GPM.
A 1-1/4" Cla-Val was installed about half-way down the piping system. It is a model 50-01, and from what I can find on their web site, it can pass a maximum continuous flow of 93 GPM.
This is obviously short of my required 119 GPM, but I don't understand how the Cla-Val operates. I'm not sure how it should be set to bypass flow when needed and not bypass it when the unit ventilators are calling. The system pump is rated at 160 GPM @ 80'.
Any suggestions on the best resolution? Should I increase the Cla-Val size? Should i add a second one? Should I do something else entirely? Where in the piping system should I put it?
Thanks for your help
The chiller has a minimum flow requirement of 119 GPM, and they want the chiller to operate even if only 1 unit ventilator is calling, which would be only about 6 GPM.
A 1-1/4" Cla-Val was installed about half-way down the piping system. It is a model 50-01, and from what I can find on their web site, it can pass a maximum continuous flow of 93 GPM.
This is obviously short of my required 119 GPM, but I don't understand how the Cla-Val operates. I'm not sure how it should be set to bypass flow when needed and not bypass it when the unit ventilators are calling. The system pump is rated at 160 GPM @ 80'.
Any suggestions on the best resolution? Should I increase the Cla-Val size? Should i add a second one? Should I do something else entirely? Where in the piping system should I put it?
Thanks for your help