raithrovers1
Industrial
- Feb 10, 2009
- 85
A technician of mine was performing battery maintenance on a UPS battery containing 2 strings of VRLA batteries. Each string had 40 jars, 240 Cells and were being float charged at approximately 530VDC. The battery is connected to a commercial type UPS (Powerware 9355) which has no isolation transformer on the input. Therefore there was high AC voltage between the posts of the battery and the ground at approximately 237VAC. (Very dangerous in my opinion but that is another topic!)
They went to take the AC ripple current going into the battery from the rectifier in the UPS. They do this by using a Fluke i410 amp clamp connected to a Fluke 87 meter clamped around the main battery positive cable. They found that they were getting very unusual readings of between 10AAC to 40AAC.
What was more unusual was that when they disconnected the amp clamp from the cable the reading on the Fluke went up to approximately 150AAC! This confused them. They proceeded to move the amp clamp all around the battery (as if it were an antenna) without connecting around any cables. At some points the meter read upwards of 300AAC! the same affect could be found when the meter was changed to DC. If you moved the meter/amp clamp away from the battery the spurious readings disappeared. The amp clamp is calibrated and is working as per design.
What is also interesting is that when internal resistance on this battery was taken using an Alber cellcorder - the cellcorder stops working. This battery has caused 3 cellcorders to be sent back for repair!
It should be noted that there is another battery in the same room as this battery that is being charged by a regular switchgear charger. This battery does not show the same affect.
Has anyone seen a phenomenon like this before?
UPS Service Manager
They went to take the AC ripple current going into the battery from the rectifier in the UPS. They do this by using a Fluke i410 amp clamp connected to a Fluke 87 meter clamped around the main battery positive cable. They found that they were getting very unusual readings of between 10AAC to 40AAC.
What was more unusual was that when they disconnected the amp clamp from the cable the reading on the Fluke went up to approximately 150AAC! This confused them. They proceeded to move the amp clamp all around the battery (as if it were an antenna) without connecting around any cables. At some points the meter read upwards of 300AAC! the same affect could be found when the meter was changed to DC. If you moved the meter/amp clamp away from the battery the spurious readings disappeared. The amp clamp is calibrated and is working as per design.
What is also interesting is that when internal resistance on this battery was taken using an Alber cellcorder - the cellcorder stops working. This battery has caused 3 cellcorders to be sent back for repair!
It should be noted that there is another battery in the same room as this battery that is being charged by a regular switchgear charger. This battery does not show the same affect.
Has anyone seen a phenomenon like this before?
UPS Service Manager