Very few solid state overload relays are capable of being used down stream of VFDs, and none of the ones Schneider sells are so rated as far as I know. Did Schneider build these bypass panels, or were they built by others? As I recall, NONE of the Schneider SSOLs are capable of being used in a circuit with a VFD, you must use a bi-metal version.
Also, as a general design rule, the OL relay on a VFD bypass is placed in the circuit so that it is only being used when the bypass starter is in use, so it would not even be in the circuit when the motor is running at 30Hz. Sounds to me as though someone built these without a good understanding of all of the potential pitfalls.