msavila (Chemical):
Mike Cronin is giving you some great, basic and essential advice that should go in your hip pocket for when you're dealing with tanks and pressure vessels.
You ask if a vacuum breaker is required for Butane storage. Again, this is a basic and elementary need that is easily resolved if you revert back to your Thermodynamics and physical properties studies. If the tank is going to be dedicated solely to Butane storage (saturated), then you need to refer to the vapor pressure of Butane:
Temp, oF Press, psia
14.000 10.119
16.000 10.590
18.000 11.078
20.000 11.584
22.000 12.107
24.000 12.649
26.000 13.210
28.000 13.790
30.000 14.390
32.000 15.010
Depending on your tank's location and elevation, the above table should tell you if you're going to generate a vacuum by allowing the tank's contents to cool down with atmospheric winter conditions. If you're located in Kingston, Jamaica, Port of Spain, Trinidad or Pucallpa, Peru I wouldn't worry about needing a vacuum breaker in a butane tank. If you're in the North Slope, you'd better have one.
Normally, I would expect to find the tank has been FV'd and I would not rest until I had the documentation that Mike Cronin lists - especially the fabrication drawings. You need these for inspection and as reference for all tank-related calculations (such as the vacuum breaker).
Art Montemayor
Spring, TX