odlanor
Electrical
- Jun 28, 2009
- 689
For comissioning , there are 2 methods to inject primary current in CT for checking the Differential Protection.
The test arrangement varies with the application.
1- On network power transformers and asynchronous machines, a low-voltage test is preferably conducted,
where low-voltage current source is used to energize the protected object, which is completely disconnected
from the network. A short-circuit bridge, which is capable of carrying the test current, is installed outside the protected zone and allows the symmetrical test current to flow.
2- For power station unit transformers and synchronous machines, the tests are performed during the current
tests, with the generator itself supplying the test current .
We use 2nd method because we always have power plant. But, we want to join 1st method for more flexibility.
Anyone have any suggestions for how to size 1st method equipment to apply on 2nd arrangement?
The test arrangement varies with the application.
1- On network power transformers and asynchronous machines, a low-voltage test is preferably conducted,
where low-voltage current source is used to energize the protected object, which is completely disconnected
from the network. A short-circuit bridge, which is capable of carrying the test current, is installed outside the protected zone and allows the symmetrical test current to flow.
2- For power station unit transformers and synchronous machines, the tests are performed during the current
tests, with the generator itself supplying the test current .
We use 2nd method because we always have power plant. But, we want to join 1st method for more flexibility.
Anyone have any suggestions for how to size 1st method equipment to apply on 2nd arrangement?