"One thing I noticed is that what you were saying about the entire suction line not being allowed to fall below 20 psi was at odds with the 'Designer's Guide to Automatic Sprinkler Systems', Robert M Gagnone which stated the 20 psi was a typical number of most authorities but that number was only required at the city main location."
Be careful.
Whatever state or locality this installation is in I would attempt an exhaustive search on whatever water distribution rules they may have.
Just two examples.
Found this for Tennessee.
Fire Pump Shop Drawings - 2006 Codes – NFPA 20, IBC, and IFC
FIRE PUMP SHOP DRAWINGS
The fire pump suction piping size must be sufficient to operate at 150 percent of rated capacity with zero psi minimum gauge pressure unless the supply is a suction tank with its base at or above the pump. [NFPA 20 5.14.3]
The Montana EPA
on page 22
8.1 WATER MAIN DESIGN
8.1.1 Pressure
All water mains, including those not designed to provide fire protection, must be sized after a hydraulic analysis based on flow demands and pressure requirements. The system must be designed to maintain a minimum normal working pressure of 35 psi. Maximum normal working pressure should not exceed 60 psi. Minimum pressure under all conditions of flow (e.g. fire flows) must be 20 psi. Minimum required pressures must be based on those occurring at ground level at the highest building sites or fire hydrant served by the proposed water mains excluding service line head losses."
"Fire flow"? Lots of discussion here on fire flows.
City of Boise, Idaho.
Safety Factors
a. All hydraulic design areas shall have a safety margin of at least 5% (cushion) on the available residual pressure at the calculated fl ow, per Idaho State Fire Marshal’s policy.
b. Where fire booster pumps are installed, the maximum design flow shall be available at not less than 5 psi at the pump suction, at 150% of rated pump capacity including any inside and outside hose or other required system demands.
Another thing to consider is a possible adverse impact a smaller 8" line may have to the total project cost.
If a small building probably no impact but for a large installation, say 100,000 sq. ft. or multiple buildings, that 30 or 40 psi you are losing on the suction line could more than be made up by having the addiitonal 40 psi available for the systems.
8" PVC will cost somewhere somewhere around $4.50 a foot while 10" might run $8.00 I'm guessing on the 10") which means 1,400 feet will cost an additional $5,000.
$5,000 isn't much money. The trench will still be a 24" wide trench so I don't see an increase in excavation costs and an extra $1,000 for fittings should more than make up the difference in fitting costs.
In a worst case scenario the added cost for the 10" suction line might be $7,000 or $8,000?
Assume a 400'x500' warehouse with heads on 10'x10' spacing. We're going to have 20,000 feet of branch line and if by having the extra 40 psi you can reduce the branch lines from 2 1/2" to 2" sch. 10 pipe the savings in the pipe ($1.80 vs $1.35) alone would be $0.45 per foot or $9,000 just for the pipe.
On couplings, assume 20' average pipe length with an extra 2 couplings per line for 300 couplings ($4.53 vs $3.95) would be another $175 and on top of this add the cost of branch line elbows etc.
Added to this would be the real added possibility of downsizing mains and risers. Of course if the facility is 10,000 sq. ft. this really isn't a factor but if it is any size at all I can easily see the cost savings achieved downstream the pump more than offset the added cost of a larger suction pipe.
Whatever happens with 40 psi more to work with the overhead pipe in the facility will be smaller and for something this size it isn't hard to envision a total overhead cost savings of $18,000 to $30,000 once you consider the additional fabrication cost and installation labor associated with larger pipe.
The larger the facility the more cost savings I envision.
Something like this would be a win-win all the way around for everyone. A superior system for less cost. Can't beat that.
In any event I would be very concerned about whatever suction pressures may be required by other authorities outside the NFPA standards.
Now that's my three cents worth.