loss of gen's excitation 2

Status
Not open for further replies.

jalover

Electrical
Dec 1, 2007
42
Pls any anybody who could give me some causes/reasons of generator losing its excitation. every time we start generator, there is no 440 volts coming in and we need to flush with 12 v battery to attain 440 volts, once the gen is loaded , say 30 kw or more, the gen load starts seesawing while in parallel with other gen set. everything was checked, avr, capacitor, rotating rectifier, current transformer & reactor, all ok. is there any other things need to be checked? i suspected that the exciter coil is damaged. what test need to be done. thanks in advance.
note : Gen ratings: 270 kw, 440 v, 60 hz.brushless.
 
Replies continue below

Recommended for you

Check the rotating diodes. Please don't double post.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
thanks a lot for all advise. we will try to carry out this helpful tips.
 