A 5MVA (rewound to 10MVA), 13.8kV steam turbine generator was operating normally. Some of the control screens started operating oddly and the operators decided to trip it off, so the power was lowered to 0.5MW and the stop valve tripped. It turned out the control screen issues were due to low DC voltage. The stop valve opened, the exciter tripped, the generator breaker did not trip, the DC trip coil started smoking and eventually burned up. The operators called an off site plant engineer for advice, were told to trip the breaker manually, saw the smoke and would not open the cabinet door. The off site plant engineer came to the site and tripped the generator breaker off manually after 45 minutes of reverse power. After some testing of the rotor and exciter and repair of the DC system the generator is back on line without apparent ill effects. (currently running for the second day) The excitation system is a Basler SSE half wave bridge with a fly back diode. The generator had about 5MVAR and 300kW going into it for the 45 minutes it was in reverse power.
Would any damage be expected on the stator? It was at 50% FLA current rating.
What amount of current was going through the rotor? Any damage? I think, not much due to it operating near sync speed, only needing enough induction to keep it near sync speed (3600RPM).
Advice and comments appreciated.