The following incidence has happened:
It was reproted that few split airconditioners (single phase) and some other (single phase) connected load got their power supply modules and control cards burnt.
These loads were fed from a three phase supply (3 phase + Neutral).
The items that burnt were distributed on all the three phases.
Investingations led to one of the two possibilites:
1. Few days ago, there was a problem reported with the Earth Fault module of the incoming breaker. The electrican the removed that earth fault module. For doing so, he had to disconnect all the three phases and the neutral wire.
2. The neutral was found loose in the four pole circuit breaker.
3. One assumption is that the electician maight have "accidently" connected a phase wire to the neutral supply! and after realizing the damage, had quietly connected the wires to the right places. And in doing so, he had left the neutral loose.
Now, to my understanding, if we assume that assumption # 3 is wrong, loose neutral is enough to introduce spikes in the system and thus blowing off power supplies.
What do you suggest?
It was reproted that few split airconditioners (single phase) and some other (single phase) connected load got their power supply modules and control cards burnt.
These loads were fed from a three phase supply (3 phase + Neutral).
The items that burnt were distributed on all the three phases.
Investingations led to one of the two possibilites:
1. Few days ago, there was a problem reported with the Earth Fault module of the incoming breaker. The electrican the removed that earth fault module. For doing so, he had to disconnect all the three phases and the neutral wire.
2. The neutral was found loose in the four pole circuit breaker.
3. One assumption is that the electician maight have "accidently" connected a phase wire to the neutral supply! and after realizing the damage, had quietly connected the wires to the right places. And in doing so, he had left the neutral loose.
Now, to my understanding, if we assume that assumption # 3 is wrong, loose neutral is enough to introduce spikes in the system and thus blowing off power supplies.
What do you suggest?