Electrifire is correct: EPR is the best. We use Kerite.
We also (based on experience) spec. 133% insulation level, with jacketed, 1/3 neutral (substation feeders). For URD single phase feeders, we specify full neutral.
If a portion of the cable is inside a conduit, then you'll have to reduce (derate) it's ampacity according to the charts. This may force you to increase the size of the cable.
We also sectionalize long runs (> 1000 ft.) by terminating three-phase main trunks into S&C PME series dead-front (safety) padmounted switches. Bt doing this, we can quickly restore power to 'downstream' areas if a 1000 ft. section becomes faulty or accidentally cut. When sectionalizing long single-phase runs, we use Nordic fiberglass enclosures with load-break junctions (four-point). Just make certain you break up the long runs.
Make sure your padmounted transformers are dead-front, loop-fed types (primary configuration) with Bayonet fuses.
On rubber products, we spec. RTE (Cooper Power Systems) and Elastimold only for elbows, etc.
When we trench, our depth of burial is below the frost line (about 6 ft. minimum). We also make certain there are no rocks, stones, or other sharp objects on or under the new cable. If possible, place sand below and above the new cable. We also place a yellow marker tape on top of the cable to ease future locating of the cable, if the need arises.
Conduit: Underneath roadways or pole risers....use schedul 80 PVC. Everywhere else: schedule 40 PVC.