My other problem is the 1:1 minimum aspect ratio required by the ICC-400, which limits the number of walls we can actually use for shear along a given line (just one wall in my case). And, because I do not have that much shear along that particular line, the required shear values are high (1500#/' IIRC) that Olylog screws won't work, and the 'holddown' rods are at each end of the particular panel instead of at the corners of the building, with 7" square plates for the compression. I use 7/8" threaded rods at 24" o/c. for shear.