As long as the total square foot area of each floor does not exceed the limit per floor, i.e. 52,000 sf for LH and OH - then you can have a single control valve, typically at the service entrance.
However, this needs to be coordinated with the fire alarm system, because the fire department (and others) will want to know where the fire is happening, which having a single control valve will not facilitate.