Hi all,
Main contractor want to operate a mobile crane on our Post-tensioned slab before grouting.
(1) I'm gonna check the slab as unbonded with lower concrete grade to match the actual strength later.
(2) What about the min As? The strands were counted as min As in the first place. Anyway the software will calculate min As for me
.
(3) I will check punching shear. Will ask them to provide steel plates.
In here structural consultants or QP, they want the grout compression strength to be the same as the slab/beams concrete grade. But in the code CP 65, the requirement is only 27 MPa. Is there any particular reason to be the same? Anyway the grout is normally in the tension zone.
Thanks