Ben29
Structural
- Aug 7, 2014
- 326
Would you be concerned about frost heave in this loading dock? The client wants to put a walk-in freezer on the loading dock (see highlighted corner of plan below). I raised concerns about frost heave since the one side of this slab is floating.
Their argument is that if the slab did heave, it would all move together, and the freezer would just move with it. I don't think this is the case. I think it is possible that the slab could crack and heave below the freezer, which would open up the joints between the insulation panels and render the freezer unusable. The proposed freezer is 4ft x 5ft.
Their argument is that if the slab did heave, it would all move together, and the freezer would just move with it. I don't think this is the case. I think it is possible that the slab could crack and heave below the freezer, which would open up the joints between the insulation panels and render the freezer unusable. The proposed freezer is 4ft x 5ft.