Apr 30, 2022 #1 james64 Electrical Joined Oct 16, 2012 Messages 46 Location CA Hello, I am working on an SPECIFICATION low voltage 100kW loadbank. Regarding rating, what specification is correct? For example, 3ph 3w or 3ph 4w.
Hello, I am working on an SPECIFICATION low voltage 100kW loadbank. Regarding rating, what specification is correct? For example, 3ph 3w or 3ph 4w.
Apr 30, 2022 #2 RRaghunath Electrical Joined Aug 19, 2002 Messages 1,745 Location IN 3ph, 4w will allow you to use the load bank for single phase loading. If your intention is to test the source with symmetrical three phase load, there is no need to connect load star point to the source switchgear, meaning you can specify 3ph, 3w. Upvote 0 Downvote