Typically, percent reactance will be constant or increase when the transformer size increases, and percent resistance will decrease.When a transformer size increases, the reactance decreases and the resistance increases.
Here we might be confusing regulation with voltage drop. By definition, regulation of a transformer is at rated load. Regulation in distribution systems is more generally defined as the percent voltage drop at whatever the load is. The voltage drop for a given load will be less with a larger transformer because the load is a lower percentage of rated load. To look at it another way, the ohmic impedance of a large transformer is less than the ohmic impedance of a smaller transformer with the same percent impedance.Now, if we have same load but a higher rating transformer as the reactance will decrease but the resistance is still less than reactance, so eventually the voltage regulation will increase.
Well, not quite right. Voltage drop is the difference between the magnitude of the sending end voltage and the magnitude of the receiving end voltage. For a transformer, you have to adjust for the transformer ratio, but the sending end voltage is the primary voltage and the receiving end voltage is the secondary voltage. The whole thing gets confused because of phase angles. The sending end voltage equals the receiving end voltage plus the impedance times the current. The voltages, the impedance, and the current all are complex values, so you have to do the math vectorially and then compare the magnitudes.But I agree %z impedance has nothing to with the voltage drop.
LGjgrist:Regulation (in pu) = 1 + R·cos(ø) + X·sin(ø) - sqrt((R·cos(ø) + X·sin(ø))² + 1 - X² - R²)