Under frequency relays, suggested by "gordonl" have found to be less effective, as it has first to wait for frequency to fall to its setting level and then has its own time delay plus intentional delay to allow the relay to ride through a power swings.
The end result is it allows the frequency to fall further below its setting, causing a worsening of the situation, leading then to the need for much larger shedding of load than required. Moreover the relays are pre-wired to trip certain load circuits and does not have any intelligence to know whether these circuits are really loaded to the extent expected. If not the situation gets further worsened, as frequency will continue to fall.
The situation could be improved by using relays with df/dt features. This also has problems as df/dt is a varying value, being subjected to the power mismatch at the instant of loss of generation. This will depend on governor response, the load on the system etc etc. One could work out a df/dt for a worst case, but will not help much. More over the relay needs to filter out harmonics, that causes some delay in its operation
At best the underfrequency relays can be used as a standby scheme to the scheme suggested by "vishalmehta". The scheme suggested by "vishalmehta" also cannot determine which feeders to trip on an intelligent basis. The best that can be done is to pre arrange a trip of certain feeders, without really knowing the extent of load on these feeders. The scheme required should dynamically rearrange the tripping sequence depending on the actual situation of load on each circuit. This is really true for a plant with varying loads, not fixed loads. Each circuit load varies from time to time.
Is there a more intelligent system, even a system that uses neural network engine, that can be trained i.e modeled to read each circuit load, generation loading at each instant and then understand, calculate, think and execute. This way the tripping can be effected quickly, and only a small requisite load and that too the right relevant circuits can be tripped.
Any ideas on any such system that one has used in their plant or have read about it.