Looking at the ABB Distribution Guide page 63 and 64 and applying it to a GrdY-GrdY bank, it appears that a balanced three phase load will split evenly between the 3 phases. Am I correct in assuming that the currents in each phase will be different and proportional to the Iz of the individual leg (more precisely the voltage regulation).
Would the same apply to a single phase load connected line to line? ie that for a 100A load current the split will not be 57.7A in each of the 2 legs
The voltage unbalance will just be reflected by a higher zero sequence current flowing in the neutral?
Would the same apply to a single phase load connected line to line? ie that for a 100A load current the split will not be 57.7A in each of the 2 legs
The voltage unbalance will just be reflected by a higher zero sequence current flowing in the neutral?