bigmig "nailed it", and I like truss jockeys, that is a good one. I worked for about a month or so for a truss company right out of school before wising up. There were three truss jockeys from various construction backgrounds, none of them engineers (actual one had a degree in electrical, still can't figure that out). They are very efficient at using the software and coming up with fast and efficient standard truss designs. Then some PE, maybe in another state (this was done), signs and seals it. So forget about getting them to do any engineering or out of the box design. I think most building codes and the Truss Plate Institute now specify the responsibilities of delegated truss engineers and the engineer of record. It is your building, you should design all the MWFRS and load path stuff.
I also like Bigmig's design, it is what I have done in the past many times for shear transfer from the roof diaphragm into the shear wall. Now for out-of-plane lateral loading of the wall, you can use your concept of using the porch roof as a diaphram or each bottom chord of the truss will really collect that load at 2' o.c. Make sure that connection at the T.O. CMU to the truss is designed for that force also. The problem is at the left side of your detail, at the truss heel, that truss plate is not designed for this drag force to get it up into the top chord and into your roof diaphragm, and per above conversations you will not get them to design for this. I think if you are only dealing with 200lbs I would put a plywood gusset just to the right of the heel with 3-5 12d in the top and bottom and call it a day.