I would say yes, a roof deck is a deck per ASCE. I treat it the same as I would a balcony or anything like that where people could conceivable be decently close together on a nice day/evening. I wouldn't really get the argument for just treating it as a 40 psf live load. I do think that treating it as 100 psf though is overkill (for a residence).This is an interesting point. Would a roof deck be considered a deck per ASCE and require 150% live load? I want to say no, but I really don't know.
I've said this before, but I always judge it on "will this deck be packed to watch fireworks" criteria. I've been on some wildly loaded decks and balconies before so that's why I almost always go to 60 psf even in residential.Balconies and decks (1.5 x 40 = 60 PSF) are listed separately from roof decks (40 PSF) in table 4.3-1. Intuitively, this makes sense in that it seems less likely that a roof deck, not as accessible as a balcony or patio deck at the same level as a floor, would be overloaded.
The argument is this is what the code says:I wouldn't really get the argument for just treating it as a 40 psf live load.
The proof is pudding, though. There are lots of things that are hard to believe but can be borne out by rigorous study. Deck failure is one of the most consequential structural failures in residential construction. If a deck fails and it's seen that the designer used anything more than CD=1.0 in design, they're likely to be crucified for it whether it was the real cause or not. So unless you have a detailed analysis of loading on decks that backs that up (and such studies are out there...just don't know if they looked at decks specifically), I would not suggest going higher than 1.0.I find it extremely difficult to believe that you would have enough massive parties on your balcony that actually excite the full 60 psf load for a cumulative 2 months over the life of the building.
I see what you're saying, I just think that stacks with the deck provision as well. We're all calling it a roof deck here. I get there's a level of semantics here, but I would say the occupancy served is a deck in a residential and thus gets the 1.5*40 psf.The argument is this is what the code says:
The only other argument I can fathom is that the code is providing minimums and you want to intentionally over-engineer because it feels good to do so, which is your prerogative.
To me, the difference is where the deck is located. If it is at the same level as a floor, then it's a deck (60 PSF). If it is a roof and is accessible as a deck, then it's 40 PSF. This is for residential. If this were an office building, then it would be 75 PSF and 50 PSF, respectively.
That's reasonable. I'll be honest I do tend to be reasonably conservative for the wood design keeping in mind that many of the details will not be constructed as indented. I'll use the method for maybe justifying a bending value, but connection design all gets done with the normal Cd values. I was using this as a bit of a code exercise to challenge some of my own engineering opinions/ideas and Cd is one where I have some gripes I suppose.dding, though. There are lots of things that are hard to believe but can be borne out by rigorous study. Deck failure is one of the most consequential structural failures in residential construction. If a deck fails and it's seen that the designer used anything more than CD=1.0 in design, they're likely to be crucified for it whether it was the real cause or not. So unless you have a detailed analysis of loading on decks that backs that up (and such studies are out there...just don't know if they looked at decks specifically), I would not suggest going higher than 1.0.
For whatever reason, it seems that decks - near/at grade, on the roof, or anywhere in between - end up going
I disagree. Using ASD makes it way more efficient from an engineering perspective as most members I size are controlled by deflection. I would probably retire if I was forced to use strength design for wood.Speaking of statistics, I get annoyed that so much of wood gets done via ASD (not from a design perspective, from a code perspective I would argue it's the default). If there is a material that would greatly benefit from an LRFD/statistics approach it is wood design. I would argue it's the default in concrete for that reason, and with woods natural variability taking a statistics approach instead of an allowable stress one makes way more sense. I will get off my soapbox now.
Wood already takes a statistical approach. Most published reference design values are the 5% exclusion. Only time average strength is used is for fire design. LRFD is fantastic, but there's nothing wrong with ASD for light/heavy timber (mass timber is a different story).Speaking of statistics, I get annoyed that so much of wood gets done via ASD (not from a design perspective, from a code perspective I would argue it's the default). If there is a material that would greatly benefit from an LRFD/statistics approach it is wood design. I would argue it's the default in concrete for that reason, and with woods natural variability taking a statistics approach instead of an allowable stress one makes way more sense. I will get off my soapbox now.
You can use LRFD per the NDS code if you really want to. I've never heard of anybody doing this, but the option does exist. FWIW, I've run through the exercise before of comparing LRFD to ASD and as a broad takeaway, I concluded there was no real difference. I suppose you could game it to use one or the other as it benefitted you, although this would be rather questionable behavior I think. If you have a copy of "Design of Wood Structures" by Breyer they do run through design examples using both methodologies.Speaking of statistics, I get annoyed that so much of wood gets done via ASD (not from a design perspective, from a code perspective I would argue it's the default). If there is a material that would greatly benefit from an LRFD/statistics approach it is wood design. I would argue it's the default in concrete for that reason, and with woods natural variability taking a statistics approach instead of an allowable stress one makes way more sense. I will get off my soapbox now.
This is a perfect comment here. The only thing I'll add is that decks usually have a lot less redundancy and "additional strength" compared to a house. No sheetrock or subfloor or family photos that help provide some alternate load paths.The proof is pudding, though. There are lots of things that are hard to believe but can be borne out by rigorous study. Deck failure is one of the most consequential structural failures in residential construction. If a deck fails and it's seen that the designer used anything more than CD=1.0 in design, they're likely to be crucified for it whether it was the real cause or not. So unless you have a detailed analysis of loading on decks that backs that up (and such studies are out there...just don't know if they looked at decks specifically), I would not suggest going higher than 1.0.
For whatever reason, it seems that decks - near/at grade, on the roof, or anywhere in between - end up going not to the good framer who just built the really nice house, but to the 2-bit hack deck builder that doesn't even know what a building code is. It's not an area that I skimp on design.
Lots of examples of deck failures that make 100 psf not seem ridiculous. What if that 180 lb person and all his friends start jumping up and down? Now you factor in lack of maintenance that could reduce capacity. I'm probably not going to try to cut hairs on a deck design to save a few bucks.Ref. ASCE 7 Table 4.3-1:
100 PSF is the equivalent of 180 lb. people standing 1'-4" apart over the entire area. I think that is ridiculous.
75 PSF is not defensible in that it does not appear anywhere in the code except for bowling alleys (!!).
Not semantics. There are clearly two distinct line items in table 4.3-1 addressing each condition.I get there's a level of semantics here, but I would say the occupancy served is a deck in a residential and thus gets the 1.5*40 psf.
At some point, you should assume others will do their job. I work with a lot of contractors and most take pride in their craftsmanship. If they don't understand or cannot achieve a detail I've provided, they usually call me. If they don't, that's on them. Yes, I detail A LOT. I've seen a lot of plans and engineering provided by others and often, they lack adequate detailing. Usually, the rationale is that there isn't enough fee to provide the site specific detailing required for the project. Most of the details are generic and don't correctly represent the actual condition. In these situations, no amount of "over engineering" will compensate for inadequate detailing.I'll be honest I do tend to be reasonably conservative for the wood design keeping in mind that many of the details will not be constructed as indented.
No amount of "over engineering" will compensate for lack of maintenance. At some point, you need to assume others will do their job.Lots of examples of deck failures that make 100 psf not seem ridiculous. What if that 180 lb person and all his friends start jumping up and down? Now you factor in lack of maintenance that could reduce capacity. I'm probably not going to try to cut hairs on a deck design to save a few bucks.
I'm not saying to over engineer just to compensate for lack of maintenance, but I know if a deck fails (and there are many examples) there are frequently serious injuries or deaths. I don't want to be scrutinized because I attempted to justify a lighter design load or high duration factor even if lack of maintenance turned out to be the root cause. The risk of misuse of a deck is very real.No amount of "over engineering" will compensate for lack of maintenance. At some point, you need to assume others will do their job.
Thanks for that.Don't think anyone brought it up here so far, but JAE had an old thread with a similar discussion and the last comment highlights the NDS commentary that directly talks about the different LDF's and what each "duration" means. Take a look at C2.3