- Nov 17, 2007
- 2
I have two 2500KW generators online in parallel. If I trip the generator breaker on one thus forcing the other generator to take on greater than 100% rated load what type (KW,KVAr) of load, or combination of, would be best to put on the generator. I believe a power factor less than .8 would be best to stay away from the excessive rotor heating limit, but would something closer to a pf of 1 be better.
The problem I found was that the generator was not able to recover with the high demand of 3100kW it leveled off at 2620kW at 56.15HZ. However, it was able to fully recover within 2sec with 2850kW (same power factor, using load banks). The point of this testing is to initiate load shedding stages.