Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations MintJulep on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Load Bearing Capacity of HSS Tube

Status
Not open for further replies.

macvicar

Automotive
Joined
May 2, 2000
Messages
33
Location
CA
I've got a situation where I need to raise a 4 legged stand about 5". I am thinking of using 2" wide pieces of 5"x5"x1/4" HSS tube. Each leg of the stand would bolt through the top horizontal surface of the tube, and the tube would be secured to the floor at the bottom with a concrete lag. The stand weighs approx. 2500lbs. How can I determine if the tube is adequate to support this load ?

Thanks

Jeff
 
AISC 360, Chapter K of the spec deals with this problem. You could also assume the max moment to be PL/4 (P=2500lbs/4, L=5") and assume the bending capacity of the tube wall to be Fy*Z, where Z=2"*.25^2/4 and Fy=yield strength of tube (usually 46ksi for HSS members). The latter method is a conservative approach, but I don't think you'll have any problems making it calc out with the loads you are dealing with.

FranzR
 
Thank-you FranzR! Since I'm not a structural engineer, would you be able to explain the calc method and result ?

Thanks

Jeff
 
Status
Not open for further replies.