Live loads in Supermarket 2

Status
Not open for further replies.

Anab

Structural
Jun 22, 2011
2
I need to desing a Supermarket on second floor, i am using 100 psf (live load) , do you know where i can confirm this value.

thanks,
 
Replies continue below

Recommended for you

IBC, Table 4.1, Retail - second floor 75 psf, plus point load of 1000# per notes.

Personally, I would consider more, that seems light for grocery store shelving and coolers.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
I have done a lot of elevated supermarkets, and the operators have usually provided their company specification. 5kPa (100psf) for the trading floor, usually 7.5kPa (150psf) to 10kPa (200psf) for the back of house stacking areas. About 15kPa (300psf) in the loading dock area. Watch out for the delivery areas. Big trucks making deliveries require highway loading.
 
Thank you Hokie66, do you have the reference for this loads, i need to print out.
I search in the web for this kind of projects (elevated supermarket) i didn't found, can you give me some links.
 
Actually, the previous reference I gave was from ASCE 7-05, but the same information is found in section 1607.1 of the IBC.

Mike McCann
MMC Engineering
Motto: KISS
Motivation: Don't ask
 
Anab,
No reference which I can give you. As I said, the quoted live loads came from proprietary design requirement specifications, in this case from the two largest Australian supermarket chains.
 
Agree with hokie also quoting the large Australian chains. 150psf for trading floors and 250psf for back of house. These requirements are client specific (very powerful clients) and would exceed the minimum values setout in IBC.
 
I spend too much time in grocery stores early in my working life, but man it made me appreciate working as an engineer!

That said, when shelves are stocked at night they often bring the pallets out and place them in the aisles. So Hokie's suggestions sound right on, since you never know where these will be placed. The canned food pallets are HEAVY!
 
kikflip,
150psf for trading floors? Is this a recent change? Used to be 5kPa, both C & WW.
 
I agree that a floor load of 200 psf in the main shopping area seems appropriate in the absence of more detailed information from the client. I check the U.S. military UFC 3-301-01 criteria whenever there is a live load not covered by ASCE/IBC. They require 200 psf for "Galley-provision storage (not refrigerated)" which is probably the closest to the situation you have.
 