Taken from NYC Code. Take a look at section(d) for walls.
Link for Code.
ARTICLE 4 LIVE LOAD REDUCTION
§[C26-903.1] 27-565 Roof loads. –
No reduction shall be permitted.
§[C26-903.2] 27-566 Floor live loads. –
The uniform live load to be used for design shall be the
basic value established in reference standard RS 9-2
multiplied by the percentages given in subdivisions (a)
through (d) of this section.
(a) Except as provided in subdivisions (b), (c), and
(d) the percentages in table 9-1 shall apply. Contributory areas
shall be computed in accordance with section 27-567 of
this article.
(b) No live load reduction shall be permitted for the
following: members and connections (other than columns,
piers, and walls) supporting floor areas used for storage
(including warehouses, library stacks, and record
storage); areas used for parking of vehicles; and areas
used as place of assembly, for manufacturing, and for
retail or wholesale sales. For columns, piers, and walls
supporting such floor areas the maximum live load
reduction shall be twenty percent.
(c) No live load reduction shall be permitted for
calculating shear stresses at the heads of columns [sic]
in flat slab or flat plate construction.
(d) In lieu of the percentages given in table 9-1, the
live load reductions for columns, piers and walls may
be taken as fifteen percent of the live load on the top
floor, increased successively at the rate of five percent
on each successive lower floor, with a maximum
reduction of fifty percent; and for girders supporting
two hundred square feet or more of floor area, the live
load reduction may be taken at fifteen percent. The
limitations of subdivisions (b), (c)and (d) of this section
shall apply.