HamburgerHelper: The table lists fault currents (5k, 10k, 15k, etc) and maximum clearing times allowed to obtain a 4, 8, 12 cal system.
Mbrooke: Our table has differences because the inputs into ArcPro differ for single-phase and three-phase arc flash. The arc gap ends up larger for three phase compared to single phase and is comparable to the method I believe NESC utilized to calculate the gap (single-phase: VLL/sqrt(3)*3*0.1, three-phase: VLL*3*0.1, the "3" is OSHA's 1910.269 App B transient overvoltage multiplier). For results on our 24.9 system at 10 cycle clearing, 3kA maximum fault current, and 15" working distance, we end up with single-phase of 0.8 cal and three phase of 2.7 cal. These were all done before IEEE 1584-2018 and ArcPro v3.0 so I'm not sure how the new standard and software (ArcPro has single & three phase modes now) will end up altering our numbers yet.