KBradio,
One solution we have used successfully on our DCS (Foxboro I/A Series) is two have two transmitters, one low range, and one high range. The transmitters have a degree of overlap.
In our application we can have a low flow condition which must be accurately monitored, but the process can also have flow levels an order of magnitude greater. The FT capable of handling the full-flow does not have the resolution for accurate control at the bottom end. We use a transfer block within the DCS logic which selects either the low range or high range FT depending on the flow. A suitable deadband on the transfer prevents excessive toggling between the two.
Basically, if the flow exceeds 95% of range on the low range FT, the measurement transfers to the high range FT. If the measurement falls below 5% of range of the high range FT, the measurement transfers to the low range FT. 95% on the low range FT equates to about 10% on the high range FT.
Hope this helps.