Working on a project where a recent short circuit study showed some existing equipment overdutied by a slight margin. Was thinkig of installing limiter lugs to reduce available short circuit current. Does anyone have experience using limiter lugs to reduce short circuit currents?

Thanks.
b
 
Limiter lugs are intended to protect the cables from short circuit damage. The do not reduce fault current; however, the clear quickly when subjected to a high fault current. They may not operate in their current-limiting range if the fault current is a lower level fault as is sometimes the case in arcing faults. One draw-back to them is that adequate space for them is necessary at their termination points. I have had difficulty with some smaller pad-mount transformers being able to accommodate them.

 
Another drawback is that they don't coordinate with anything downstream.
 