NJ1
I respectfully disagree. My biggest issue with limited area sprinkler systems is they are employed to resolve issues in the IBC for incidential occupancies. Someone using a limited area system for the protection of a laboratory, spray booth, or a rubbish chute room housing a dumpster full of trash or linen and expecting a 10 GPM sprinkler to protect the hazard needs to be working in an industry where they use the statement "you want fries with that." As a former code official, I rarely allowed these systems, and when I did, it was for light hazard uses.
Finally, if a system is not reliable, why select it? Our job is not to appease the code official - its to provide a minimum level of protection that is reliable and meets the requirements of the design standard as well as the adopted construction code.