Hopefully this is the right forum-I have a client (municipal) who serves domestic water to an established appartment complex. I was called to look at a magnetic flow transmitter, installed eight yrs. ago, within the complex with regard to continual lightning damage of the flowmeter electronics, according to the city electrician 1 or 2 times a yr over the last 3-4 yrs.
The meter is located in an underground vault, pvc pipe outside the vault, cast iron within the vault. The water line runs adjacent to a road running thru the complex. The electroncs for the meter are in a polycarbonate box 6' above grade. A 20a 120v ciruit is fed from a building on the other side of the street underground to the enclosure.
Examining a couple of "fried" circuit boards (their mounted mounted above grade), the damage is near the connector that feeds low v D.C. to the coils on the meter, not near, circuit wise, to the 120v input to the board. Also damage to the terminal strip at the underground portion of the meter.
I'm wondering now if the damage may not be entering from the utility power- could it somehow be propagating from the vault? There is no 120v power at the uderground portion of the meter.
The surroundings of the above-grade electroncs seemed tame enough- an 8 foot or so berm behind the installation and a couple of 15 foot or so trees within 20 feet.
The meter is located in an underground vault, pvc pipe outside the vault, cast iron within the vault. The water line runs adjacent to a road running thru the complex. The electroncs for the meter are in a polycarbonate box 6' above grade. A 20a 120v ciruit is fed from a building on the other side of the street underground to the enclosure.
Examining a couple of "fried" circuit boards (their mounted mounted above grade), the damage is near the connector that feeds low v D.C. to the coils on the meter, not near, circuit wise, to the 120v input to the board. Also damage to the terminal strip at the underground portion of the meter.
I'm wondering now if the damage may not be entering from the utility power- could it somehow be propagating from the vault? There is no 120v power at the uderground portion of the meter.
The surroundings of the above-grade electroncs seemed tame enough- an 8 foot or so berm behind the installation and a couple of 15 foot or so trees within 20 feet.