Robin7
Structural
- Mar 27, 2012
- 3
We have been asked to review and engineer a steel roof deck support detail proposed by the steel truss fabricator as an alternate to the detail provided by the EOR. The original detail by the EOR is a continuous 1/4” bent steel plate welded to a continuous embed pate with headed studs. The proposed detail is a post-installed light gauge bent plate (similar to a hat channel) attached to the concrete beam using Tapcons. The wind loads are 150 lb/ft uplift (net) and 285 lb/ft diaphragm. We are assuming the wall is braced by the tie beam (not the deck) at this time so no wind loads perpendicular to the deck (we need the EOR to verify this). Has anyone used light gauge steel for steel roof deck bearing or have any other ideas on how the deck support could be post-installed? Sketches of the current detail and proposed detail are attached for clarification.