ChasBeans1,
Im from Sydney Australia, so im more familiar with Australian Standard requirements. Specifically AS1668.2 - mechanical ventilation for indoor air quality. Should be a derivative of ASHRAE ventilation standards (from experience).
Anyway, for a computer room where the number of occupance for the space is not known, number of occupants should be taken based on 25m2 nett floor area per person. Fresh air requirement is 10l/s per person generally, however there is provision for fresh air to be reduced to 7.5l/s per person where high efficiency filters are used.
Just a note, i agree with previous posts that fresh air to the computer room may be via a dedicated central AHU providing tempered fresh air or fresh air ducting to the space directly from outside, or even off a cooling only system which has a percentage of outside air mixture that is being fed into computer room to comply with code requirements. IE a cooling only system with 50% outside air mixture, with computer room requiring 25l/s of fresh air for one occupant might typically have 50l/s of conditioned cool air ducted to it.. (not ideal, but definitely a workaround).