I understand the levelling nuts underside the baseplate for levelling purposes . The use of levelling nuts under the baseplate is not acceptable for the vibrating equipment foundations.
I copied and pasted my respond to thread407-462146
(..
HTURKAK (Structural)3 Jul 20 08:27
I just want to remind some critical points for grouting of vibrating machinery for more than 50 HP..
i =The grout shall support the equipment skid. The use of plate shims for adjustment will hinder this concept.
İİ=The use of adjustment nut underside the baseplate for levelling purpose , is not a good idea. This will hinder the loading of grout and tightening of the anchor nut will not be effective.
İİİ=
The ( pump mass + grout mass + foundation mass ) shall vibrate as a unique mass to minimize the pump vibration effects. In order to justify this, the anchor bolt sahll be preloaded to a level , such that ,the concrete foundation will receive compression stress around tension strength or the preload shall overcome an externally applied cyclic load.
The following picture is copy and paste from the book ;The Grouting Handbook A Step-by-Step Guide for Foundation
Design and Machinery Installation (Donald M. Harrison ))
IMO, you have two options; either use levelling screw set up as shown on the picture or plastic levelling nuts..