We have Battery Banks for UPS which has critical load. The battery are Power Safe Lead acid Sealed batteries. THe Installation is 5 yrs old.There are two banks each having 66 cells.Each bank has two strings of 33 cells each
During last year Battery discharge test we found 70 batteries out of 132 faulty. The same were replaced with the new batteries. The Secification of the batteries was same as before.During the commissioning of the new batteries again we dd load bank dischage test of all batteries.we found that out of old batteries ( which were healthy last time) 10 batteries have failed.
The battery type is 12V80.We have made one complete bank of new cells. My questions are
1. We are doing the Load Bank discharge test of Batteries every year. Is this frequency ok
2. At this rate each year we may find some old batteries faulty so what is the solution.
I have read that the Life of Lead Acid cells are 5-7 yrs.
During last year Battery discharge test we found 70 batteries out of 132 faulty. The same were replaced with the new batteries. The Secification of the batteries was same as before.During the commissioning of the new batteries again we dd load bank dischage test of all batteries.we found that out of old batteries ( which were healthy last time) 10 batteries have failed.