if you are working out over turning then you are not concerned with modulus modulus. subgrade reactions are used for determining displacement and reactions.
If you you need to work out over turning then you need to be assessing the overturning force, which is your wind load. And your resisting force, which is weight of concrete and passive resistance.
Your embedment is only 1m deep. Many engineers ignore passive for the upper 1m as the ground could be desiccated or subject to freeze/thaw.
On that basis I would only use weight of concrete as resisting force. If you are really pushed to make that work and you are confident there is no desiccation or freeze thaw then maybe you could use the bottom 0.5 as passive.