ajk1
- Apr 22, 2011
- 1,791
In 1956±, what was the practice for calculating the lateral earth pressure against a basement wall?
From archival calculation notes on microfilm, I see the calculations were carried out based on 100 pounds per cubic soil weight, a lateral earth pressure coefficient of 0.30, no live load surcharge (although the wall is tight adjacent a wide sidewalk of a main street) and by the working stress design method and a rebar working stress of 20,000 psi. Today we would design for 130 pcf soil and probably a lateral pressure coefficient of 0.50, although I am not sure exactly what would be used for clay, and probably a live load surcharge of 200 psf, but at least 100 psf, but I cannot get the wall to figure for this by a wide margin, even if I do it by LSD. The wall was poured against wood lagging and steel soldier piles at 8 foot centres. There is a relatively wide (0.90 mm) horizontal crack at mid-height of several bays of lower basement wall, but not in all bays There are 2 below grade levels of parking. The wall was reinforced with #6 @ 21" verical inside face rebar, and also had heavier out side face vertical rebar at the negative moment region.
I am interested in all comments, but particularly if you had experience in the Toronto area in about that era.
To reiterate, the question is what was the design practice with respect to soil weight and lateral pressure coefficient in about 1956 for basement walls?