Lateral Loads for Large Live/Dead Load Ratio
theonlynamenottaken
228
I've designed several "roof-top deck" structures for 100 year old, brick town-square buildings recently. The structures are stand alone (from the brick building structure), with columns extending down to new foundation. BUT, they usually have very large live/dead load ratios and they have absolutely no wind area. What do you use as your lateral load?
Seismic is not the lateral load I most worry about. It is the group of people "swaying" forces I'm pondering. You know, a bunch of people dancing together - which is a very real possibility for roof-top assembly areas at restaurants (wedding receptions).
What I have been using for lateral load is a percentage of the live load. Of course, this isn't identified in codes or literature anywhere. Using ASCE 7 I can easily determine the seismic response coefficients and base shears based off of structure dead loads, but this doesn't seem to be enough load. Also, I worry about service drifts - i.e., excessive drift just from people shifting their weight from side to side. ASCE provides "people sway" lateral forces for stadium seating/bleachers, but those aren't directly applicable...
Sure, I can set a service drift limit - say H/400, 500, etc. But what load do you use to evaluate that??
Any thoughts???
Include some portion of your LL in your mass for determining your seismic load.
That seems like an "allowable stress" approach to this dilemma. Arbitrarily selecting a portion of LL to include in seismic calcs to determine a non-seismic loading. And, how much is "some portion"?
StructuralEIT - Let me clarify. I do include a portion (usually 50%) of the LL in the seismic DL. But, in this part of the country where Cs is usually less than 10% I fear that this increased seismic load is still not as large as the "people induced" lateral load would be....
Are you concerned about the vibration of the roof system? If the roof is accessible, I guess your roof deck has a concrete fill.
I don't think a bunch people partying on a roof top would excite the struture to be concerned about the lateral effects.
What about applying a code wind load to the "area" of the group of people on the deck? i.e. human sails.
Otherwise, I would suggest doing what you are doing and that is to take a percentage of the dead load and live load as a lateral force.
In low seismic areas (SDC A) you get 0.01 x W for the required lateral seismic demand on the structure.
In my city, the code has been amended to use 0.02W.
Perhaps you could estimate a lateral surge force from a group of people all running to one side of the floor and stopping at once. This might be somewhat analogous to the 20% lateral force required by AISC for crane side-loads.
Just some thoughts.
even better, how 'bout applying the stadium sway loading from the IBC live load section?
I second Galambos opinion of using stadium bleacher sway loads. We have done this in the past. Atleast you are following a recommendation from the code, in case anyone questions it.